Electrical Question 480V 3 phase

Postby tmays » Thu Mar 02, 2023 12:03 pm

Will the 15 kva 3 phase 480V transformer run the 3 phase 480V 14400-19000 watt piece of equipment? I don’t know the power factor of the piece of equipment. Thanks

B950AD1A-C6C4-46C1-984A-3DC323984DF2.jpeg
B950AD1A-C6C4-46C1-984A-3DC323984DF2.jpeg (23.52 KiB) Viewed 4447 times
CF67522B-D5AC-473B-90BD-379D21891F86.jpeg
CF67522B-D5AC-473B-90BD-379D21891F86.jpeg (21.73 KiB) Viewed 4447 times
Thomas

User avatar
tmays
10+ Years
10+ Years
Posts: 3417
Joined: Wed May 11, 2011 8:59 pm
Zip Code: 39154
Tractors Owned: 1969 Farmall Cub
1952 Cub
1942 Farmall H
Location: Raymond, MS

Re: Electrical Question 480V 3 phase

Postby tmays » Thu Mar 02, 2023 12:05 pm

Sorry for the pic orientations. I can never tell when it will do that
Thomas

SamsFarm
501 Club
501 Club
Posts: 1853
Joined: Wed Jan 20, 2021 8:21 pm
Zip Code: 44410
Tractors Owned: 1968 Cub Fast Hitch
LF-1 Platform Carrier
144 Cultivators
L-F194 Plow(s)
F38 Disk
L-F3 Spring Tooth Harrow
CS Bell No. 60 Grain Mill on a unmodified Fast Hitch Disk hitch prong
Home Made Fast Hitch Potato Plow
54A Blade

Couple 1948 Cubs
172 Runner Planter
53 Fertilizer
Cub-3 Field Cultivator
Cub-189 Two Way Plow
Cub-22 Sickle Bar Mower
Mechanical Transplanter with side mount barrel (needs a fast hitch adapter) :)

Misc Belly Mowers

Wish List
International 100 Fast Hitch Blade
Mott Fast Hitch Flail Mower

Wish Wish Wish List
Fast Hitch Rotary Hoe
4E hammer mill
Location: Ne Ohio

Re: Electrical Question 480V 3 phase

Postby SamsFarm » Thu Mar 02, 2023 1:39 pm

I would think someone in the maintenance / millrights trades could tell you.

Your pics are too blury to read, especially when zoomed in enough to see.

I expect a few phone calls to the manufactures of the transformer and whatever piece of equipment you are trying to connect is in order.

In my limited experience, I am guessing your answer is no, it will not work.

15kva with a pf of 1 is 15000watts
15kva with a pf of .9 is 13,500watts

I could be wrong, so that is why I recommend some calls to the mfg.

Ps,
That is a lot of power!
1968 Cub Fast-Hitch

User avatar
tmays
10+ Years
10+ Years
Posts: 3417
Joined: Wed May 11, 2011 8:59 pm
Zip Code: 39154
Tractors Owned: 1969 Farmall Cub
1952 Cub
1942 Farmall H
Location: Raymond, MS

Re: Electrical Question 480V 3 phase

Postby tmays » Thu Mar 02, 2023 1:51 pm

SamsFarm wrote:
15kva with a pf of 1 is 15000watts
15kva with a pf of .9 is 13,500watts

I could be wrong, so that is why I recommend some calls to the mfg.

Ps,
That is a lot of power!


Well I’m the maintenance guy. But I’ve never installed a transformer. Was leaning toward the won’t work, myself. As far as the amount of power, yeah it’s a fancy combi oven that we pulled from a remodel job and just in storage. And have a need for one at a old school that doesn’t have enough voltage available
Thomas

User avatar
Bill V in Md
10+ Years
10+ Years
Posts: 1126
Joined: Sun Feb 02, 2003 6:51 pm
Zip Code: 21228
Tractors Owned: 1948 Farmall Cub
LT1045 Cub Cadet
Circle of Safety: Y
Location: MD, Catonsville

Re: Electrical Question 480V 3 phase

Postby Bill V in Md » Thu Mar 02, 2023 2:19 pm

I agree the answer is no that particular transformer will not work. The full load amps for a 15 kva 3 ph 480v transformer is 18 amps. I am not sure what kind of equipment that is that you are trying to power, but assuming the power factor is 85% (typical for electric motors), the current draw would be 27 amps, based on a power output of 19kw. Other more resistive loads would have a lower power factor and that would increase the current draw. Even at the lower power output of 14.4 kw, the current draw would be about 20 amps.
Bill VanHooser
Cub 54 Blade, Cub 193 Moldboard Plow, Cub 28A Disc Harrow
Circle of Safety

Eugene
Team Cub Mentor
Team Cub Mentor
Posts: 20381
Joined: Fri Jul 02, 2004 9:52 pm
Zip Code: 65051
Circle of Safety: Y
Location: Mo. Linn

Re: Electrical Question 480V 3 phase

Postby Eugene » Thu Mar 02, 2023 3:47 pm

I ran the numbers myself and said it won't work.

Over lunch I had my son, a maintenance electrician, rotate the photos and look over the numbers. He said no.

I think you will need a local electrician to look over the possible installation.
I have an excuse. CRS.

User avatar
tmays
10+ Years
10+ Years
Posts: 3417
Joined: Wed May 11, 2011 8:59 pm
Zip Code: 39154
Tractors Owned: 1969 Farmall Cub
1952 Cub
1942 Farmall H
Location: Raymond, MS

Re: Electrical Question 480V 3 phase

Postby tmays » Thu Mar 02, 2023 4:49 pm

Thanks, fellers. I posed the question because it’s a transformer that’s not being used and an oven not being used. I’ll let the boss know. I’ll check the cost of a new transformer, but one that size won’t be cheap.
Thomas

SamsFarm
501 Club
501 Club
Posts: 1853
Joined: Wed Jan 20, 2021 8:21 pm
Zip Code: 44410
Tractors Owned: 1968 Cub Fast Hitch
LF-1 Platform Carrier
144 Cultivators
L-F194 Plow(s)
F38 Disk
L-F3 Spring Tooth Harrow
CS Bell No. 60 Grain Mill on a unmodified Fast Hitch Disk hitch prong
Home Made Fast Hitch Potato Plow
54A Blade

Couple 1948 Cubs
172 Runner Planter
53 Fertilizer
Cub-3 Field Cultivator
Cub-189 Two Way Plow
Cub-22 Sickle Bar Mower
Mechanical Transplanter with side mount barrel (needs a fast hitch adapter) :)

Misc Belly Mowers

Wish List
International 100 Fast Hitch Blade
Mott Fast Hitch Flail Mower

Wish Wish Wish List
Fast Hitch Rotary Hoe
4E hammer mill
Location: Ne Ohio

Re: Electrical Question 480V 3 phase

Postby SamsFarm » Fri Mar 03, 2023 2:28 pm

Bill V in Md wrote:I agree the answer is no that particular transformer will not work. The full load amps for a 15 kva 3 ph 480v transformer is 18 amps. I am not sure what kind of equipment that is that you are trying to power, but assuming the power factor is 85% (typical for electric motors), the current draw would be 27 amps, based on a power output of 19kw. Other more resistive loads would have a lower power factor and that would increase the current draw. Even at the lower power output of 14.4 kw, the current draw would be about 20 amps.


Wondering how you came up with your amp ratings.

I am no electrical guru, but thought Ohm's law was Volts x Amps = Watts

14,400w / 480v would equal 30 amps, unless I am missing something.

Maybe something with the 3 phase that changes the amp draw. ??? Please explain!
1968 Cub Fast-Hitch

User avatar
Bill V in Md
10+ Years
10+ Years
Posts: 1126
Joined: Sun Feb 02, 2003 6:51 pm
Zip Code: 21228
Tractors Owned: 1948 Farmall Cub
LT1045 Cub Cadet
Circle of Safety: Y
Location: MD, Catonsville

Re: Electrical Question 480V 3 phase

Postby Bill V in Md » Fri Mar 03, 2023 3:48 pm

SamsFarm wrote:
Bill V in Md wrote:I agree the answer is no that particular transformer will not work. The full load amps for a 15 kva 3 ph 480v transformer is 18 amps. I am not sure what kind of equipment that is that you are trying to power, but assuming the power factor is 85% (typical for electric motors), the current draw would be 27 amps, based on a power output of 19kw. Other more resistive loads would have a lower power factor and that would increase the current draw. Even at the lower power output of 14.4 kw, the current draw would be about 20 amps.


Wondering how you came up with your amp ratings.

I am no electrical guru, but thought Ohm's law was Volts x Amps = Watts

14,400w / 480v would equal 30 amps, unless I am missing something.

Maybe something with the 3 phase that changes the amp draw. ??? Please explain!


I actually consulted published data for the capacity of a 15 kva transformer and found that it was 18 amps.

But to your point, power in any balanced polyphase system equals line voltage times line current times the power factor times the square root of the number of phases: Assuming a PF = .85 and solving for current;
I = 14.400 / (480 x .85 x 1.73) or 20.4 Amps
Bill VanHooser
Cub 54 Blade, Cub 193 Moldboard Plow, Cub 28A Disc Harrow
Circle of Safety

SamsFarm
501 Club
501 Club
Posts: 1853
Joined: Wed Jan 20, 2021 8:21 pm
Zip Code: 44410
Tractors Owned: 1968 Cub Fast Hitch
LF-1 Platform Carrier
144 Cultivators
L-F194 Plow(s)
F38 Disk
L-F3 Spring Tooth Harrow
CS Bell No. 60 Grain Mill on a unmodified Fast Hitch Disk hitch prong
Home Made Fast Hitch Potato Plow
54A Blade

Couple 1948 Cubs
172 Runner Planter
53 Fertilizer
Cub-3 Field Cultivator
Cub-189 Two Way Plow
Cub-22 Sickle Bar Mower
Mechanical Transplanter with side mount barrel (needs a fast hitch adapter) :)

Misc Belly Mowers

Wish List
International 100 Fast Hitch Blade
Mott Fast Hitch Flail Mower

Wish Wish Wish List
Fast Hitch Rotary Hoe
4E hammer mill
Location: Ne Ohio

Re: Electrical Question 480V 3 phase

Postby SamsFarm » Sat Mar 04, 2023 5:27 pm

Thank you Bill V
1968 Cub Fast-Hitch


  • Similar Topics
    Replies
    Views
    Last post

Return to “Off Topic”

Who is online

Users browsing this forum: Majestic-12 [Bot] and 0 guests